DATE: 27/11/2011DOC.MIE92093 REV. 1.35
8/19/2019 Bo thu ro le T1000
2/108
DOC. MIE92093 Rev. 1.34 Page 2 of 108
REVISIONS SUMMARY VISA
N PAGE DATE
1 All 20/10/2008 Issued Lodi
1.28 26 2/02/2010 Added the paragraph
test results handling
Lodi
1.28
-1
17, 37 1/10/2010 Added the TD1000
model and the 15 Hz
Lodi
1.34 11 –13;41
7/9/2011 Revised to issue 1.34;removed the serial
I/F
Lodi
1.35 39 27/11/2011 Added the FT1000
connection
Lodi
8/19/2019 Bo thu ro le T1000
3/108
DOC. MIE92093 Rev. 1.34 Page 3 of 108
SHORT FOREWORD ...................................................................................... 5
INTRODUCTION ............................................................................................. 6
1 TEST SET EXPLANATION ...................................................................... 9
1.1 CONNECTION TO THE RELAY AND POWER-ON ........................................... 9
1.2 TEST CONTROL .......................................................................................... 10
1.3 CURRENT GENERATION ............................................................................. 14
1.4 AC VOLTAGE GENERATION FROM MAIN OUTPUT ..................................... 18
1.5 DC VOLTAGE GENERATION FROM MAIN OUTPUT .................................... 18
1.6 AC VOLTAGE GENERATION FROM THE AUXILIARY OUTPUT..................... 19
1.7 DC VOLTAGE GENERATION FROM THE AUXILIARY OUTPUT .................... 23
1.8 AUXILIARY CONTACTS .............................................................................. 24
1.9 THE TIMER ................................................................................................. 24
1.10 FINDING RELAY THRESHOLDS ................................................................ 26
1.10.1. Introduction ........................................................................ 26
1.10.2. First threshold trip and drop-off ............................... 27
1.10.3. Second threshold trip and drop-off ......................... 28
1.11 FINDING RELAY TIMINGS ....................................................................... 28
1.12 TEST RESULTS HANDLING ...................................................................... 30
1.13 BASIC TEST PRINCIPLES ........................................................................ 32
1 13 1 I d i
8/19/2019 Bo thu ro le T1000
4/108
DOC. MIE92093 Rev. 1.34 Page 4 of 108
3.2.6 CONV T1000 board PWA11401 (16)........................... 69
3.2.7 INTE ON-OFF T 1000 board PWA11400 (7) ........... 70
3.2.8 MICR T 1000 board PWA41300 (15) .......................... 70 3.2.9 AP-50 AC Voltage board PWA11396 (10) ............... 70
3.2.10 Protection fuses ................................................................... 70
3.2.11 Connectors summary ........................................................ 71
4 THE HELL, IT DOESN’T WORK ......................................................... 73
4.1 INTRODUCTION ......................................................................................... 73 4.2 ERROR MESSAGES .................................................................................... 74
4.3 TROUBLE SHOOTING ................................................................................. 76
4.3.1 Auxiliary supplies .................................................................. 79
4.3.2 No power at power-on ........................................................ 79
4.4 AUXILIARY DC VOLTAGE FAULT ..................................................... 80
4.5 AUXILIARY AC VOLTAGE FAULT ............................................................... 83 4.6 NO OUTPUT FROM THE MAIN CURRENT AND VOLTAGE ........................... 84
4.7 DOES NOT MEASURE THE MAIN CURRENT ............................................... 85
4.8 THE BACKLIGHT OR THE DISPLAY DOES NOT OPERATE .......................... 85
4.9 THE AC VOLTAGE MEASUREMENT IS NOT STABLE .................................. 88
4.10 THE TRIP INPUT IS NOT DETECTED OR TIMING ERROR ........................ 88
O S G G 90
8/19/2019 Bo thu ro le T1000
5/108
DOC. MIE92093 Rev. 1.34 Page 5 of 108
SHORT FOREWORD
Dear T 1000 PLUS user,
I often wondered why the user’s manual is not very much used,
even if it includes valuable information. As me too I am a user of
such manuals, the answer I have given myself is that valuable
information are concealed somewhere in the thick thing, and I donot have time to waste to find it. So, either the manual is actually
of help, or I ignore it.
This is why I decided to split the T 1000 PLUS manual in three:
specification, with all performance details; application manual,
with instructions about how to use it one its operation isunderstood; introductory guide, with the device description and
basic information. The idea is that you may read once the
introductory guide or the specification, while you need to follow
application examples more than once; so, why not to split the
manual in three?
8/19/2019 Bo thu ro le T1000
6/108
DOC. MIE92093 Rev. 1.34 Page 6 of 108
INTRODUCTION
The single phase relay test set mod. T 1000 PLUS is suited for the
testing and adjustments of the following types of relays; the table
lists also the paragraph that explains the test procedure.
Type of relay IEEE code PARAGRAPH
- Distance* 21 1.12- Synchronizing 25 1.8
- Over/under-voltage 27 - 59 1.2
- Power, varmetric or wattmetric 32 - 92 1.4
- Under current 37 1.1
- Loss of field 40 1.10
- Reverse phase current 46 1.4
- Instantaneous overcurrent 50 1.1
- Ground fault 50N 1.1
- Timed overcurrent 51 1.1
- Power factor 55 1.4
- Directional overcurrent 67 1.5
8/19/2019 Bo thu ro le T1000
7/108
DOC. MIE92093 Rev. 1.34 Page 7 of 108
The instrument contains three separate generators:
. Main generator, which generates either AC current, AC voltage;DC voltage;
. Auxiliary a.c voltage generator, that generates an independent,
phase shifting a.c voltage;
. Auxiliary DC voltage generator, that generates the DC voltage
that feeds the relay under test.
All outputs are adjustable and metered at the meantime on the
large, graphic LCD display. With the multi-purpose knob and the
LCD display it is possible to enter the MENU mode that allows
setting many functions, which make T 1000 PLUS a very powerful
testing device, with manual and semi-automatic testing
capabilities, and with the possibility to transfer test results to aPC via the USB interface. These results can be recorded,
displayed and analyzed by the powerful TDMS software, which
operates with all WINDOWS versions, and allows creating a data
base of all tests in the plant.
8/19/2019 Bo thu ro le T1000
8/108
DOC. MIE92093 Rev. 1.34 Page 8 of 108
the multi-function knob. With less power, the maximum voltage is
reduced by a factor of 4.4; the adjustment span on the knob is
increased accordingly.
Additional features are:
. Two meters, current and voltage, with independent inputs, allow
measuring T 1000 PLUS outputs or any other source;
. Two auxiliary contacts, that allow simulating the circuit breaker;
. A set of resistors allows easing output adjustment.
The instrument is housed in a transportable aluminum box, that
is provided with removable cover and handles for ease of
transportation.
NOTE: WINDOWS is a trademark of MICROSOFT inc.
8/19/2019 Bo thu ro le T1000
9/108
DOC. MIE92093 Rev. 1.34 Page 9 of 108
1 TEST SET EXPLANATION
1.1 CONNECTION TO THE RELAY AND POWER -ON
At first, be sure that the main control knob (6) is turned (rotated)
to the zero position (complete counter-clockwise). The reason is
that the current generator is actually a high current voltagegenerator. If the output is connected to the load (typically low
impedance), as soon as the test is started, a very high current
can circulate in the circuit.
Next connect the mains supply cable to the instrument and then
to the supply. THE SUPPLY VOLTAGE MUST BE THE SAME ASINDICATED ON THE PLATE.
Power-on T 1000 PLUS: a diagnostic sequence controls:
. Key microprocessor board components;
. Auxiliary supply voltages.
8/19/2019 Bo thu ro le T1000
10/108
DOC. MIE92093 Rev. 1.34 Page 10 of 108
. Fuse on the mains supply.
. Thermal NTC sensor on the main and auxiliary transformers. In
case of over-temperature, an alarm message is displayed.
. Thermal sensors on the SCR that controls current injection, and
of the internal temperature. In case of over-temperature, an
alarm message is displayed.
1.2 TEST CONTROL
The T 1000 PLUS front panel is explained in next paragraph.
T 1000 PLUS generation is controlled by the two keys < (55) and> (56).
Settings and menu selections are controlled by the multi-function
knob with switch (22): see next paragraph for menu selections
description. At power-on T 1000 PLUS generation is OFF, as
8/19/2019 Bo thu ro le T1000
11/108
DOC. MIE92093 Rev. 1.34 Page 11 of 108
according to selections; Vdc aux is generated. In this condition,
any trip of Stop input is ignored.
. ON: timer starts; main outputs are generated; Vac aux has thefault value; Vdc aux does not change. In this situation any trip at
Stop input is detected; it is possible to verify and memorize the
relay threshold, both trip and reset. As the relay trips, the TRIP
LED (43) turns on for 5 seconds; during 5 seconds, parameters at
trip are displayed; then, the standard measurement is restored.
Test results can be saved according to Save selections.. From OFF to ON + TIME: main outputs are generated and thetimer starts according to selections; as Stop trips or resets, T
1000 PLUS returns to OFF, the TRIP LED (43) turns on and
parameters at trip are displayed until ON or ON+TIME are
selected. Test results can be saved according to Save selections.
. From ON to OFF + TIME: main outputs are removed the timerstarts according to selections; as STOP is sensed, T 1000 PLUSreturns OFF, the TRIP LED (43) turns on and parameters at trip
are displayed until ON or ON+TIME are selected. Test results can
be saved according to Save selections.
8/19/2019 Bo thu ro le T1000
12/108
DOC. MIE92093 Rev. 1.34 Page 12 of 108
. Trip + pulse time: the timer measures the delay and the
duration of the trip impulse.
. Reclose test. It is possible to select via menu the test of areclosing scheme. Two selections are available, according to the
type of recloser under test.
In the first operating mode, T1000 PLUS is connected as follows:
Trip command to the STOP input; Reclose command to the START
input. As Reclose is detected, the test set automatically applies
FAUL
RELAY
CB
MAX TIME
0.1 s
DELAY
8/19/2019 Bo thu ro le T1000
13/108
DOC. MIE92093 Rev. 1.34 Page 13 of 108
FAULT 1 2
TRIP (STOP) 1 2
RECLOSE 1
(START)
TIME MEAS.
Figure 4: Measure of Delay and Reclose times
The second operating mode refers to pole mounted CB’s. In this
mode, there is only one signal coming from the device under test:
the position of the CB. In this mode, the operation is the
following.
D1 R1 D2 R2
TD
8/19/2019 Bo thu ro le T1000
14/108
DOC. MIE92093 Rev. 1.34 Page 14 of 108
. Timed: in all modes (ON; ON+TIME; OFF+TIME), fault outputs
are generated for the programmed maximum time; after this, T
1000 PLUS returns OFF. Any trip after this time is not sensed.. External. This mode allows for the synchronization of more T
1000 PLUS: they start generating upon reception of the START
input, that is selected in External mode.
. OFF delay: fault parameters can be maintained for the specified
time after relay trips: this allows simulating the circuit breaker
delay.
Test power selection: it allows reducing the available power; this
increases the adjustment sensitivity for low current tests on low
burden relays.
Save selections:. No automatic saving.
. Automatic test data saving as relay trips. A pop-up window
confirms the saving and tells the test number.
. Test data can be saved after confirmation. After relay trip,
pressing the multi-function knob the operator can save the test
8/19/2019 Bo thu ro le T1000
15/108
8/19/2019 Bo thu ro le T1000
16/108
DOC. MIE92093 Rev. 1.34 Page 16 of 108
40 12 1.6 3.2
20 2.6 5.2
30 4 840 5.2 10.4
60 7.8 15.6
80 10.5 N.A.
10 5 2.2 4.4
7.5 3.3 6.6
10 4.4 8.815 6.6 13.2
20 8.8 N.A.
NOTE: with the supply of 115 V, the current sunk at maximumcurrent outputs is too high; so, these outputs are not available.
2) MAXIMUM POWER 60 VA
RANGEA AC
CURRENTOUTPUT
A
MAXIMUMPOWER
VA
LOADTIME
s
RECOVERYTIMEmin
8/19/2019 Bo thu ro le T1000
17/108
DOC. MIE92093 Rev. 1.34 Page 17 of 108
. Select by the push-button (57) the measurement on the desired
output sockets (13), according to the maximum current to be
generated: the LED turns on; the AC voltage value is displayed.. Connect the relay to be tested to sockets (13). Consider that for
tests of 40 A up it is necessary to connect the relay by a wire
having at least a cross section of 10 sq. mm; for lower currents, a
cross section of 2.5 sq. mm can be used.
. Press ON and adjust the output current to the desired value with
knob (6).. After you have started the test, if the burden is a short circuitmade of a short cable, you measure at zero knob position a
current that usually is less than 3% of the range. This value doesnot influence at all the measurement of the current you aregenerating: it is not an error of the measurement
instrument. If the current is a problem, select the 60 VA power,and/or connect resistors in series.. There are two more possible problems: the desired current
cannot be reached; the adjustment is difficult because the current
is reached too easily.
.. If it is impossible to reach the desired value, this is because the
8/19/2019 Bo thu ro le T1000
18/108
DOC. MIE92093 Rev. 1.34 Page 18 of 108
1.4 AC VOLTAGE GENERATION FROM MAIN OUTPUT
If the current of 3.5 A is exceeded on main AC voltage output,the generation is interrupted, and the operator is warned by an
alarm message.
This generator serves for the test of synchronism relays, where
two voltages are necessary. The procedure is the following.
. At first, be sure that the main control knob (6) is turned
(rotated) to the zero position (complete counter-clockwise).
. Power-on T 1000 PLUS.
. Select by the push-button (57) the measurement on output
sockets (60): the LED turns on; the AC voltage value is displayed.
. There are two ranges available: 250 V (full power); 57 V(reduced power). The default at power-on is full power; if 57 V
are enough, for a better adjustment, reduce the voltage as
follows.
TEST CONTROL > TEST POWER (Power) ESC. Adjust the output voltage to the desired value with knob (6).
8/19/2019 Bo thu ro le T1000
19/108
DOC. MIE92093 Rev. 1.34 Page 19 of 108
. Select by the push-button (57) the measurement on output
sockets (61): the LED turns on; the DC voltage value is
displayed.. There are two ranges available: 300 V at 300 W continuous (full
power); 68 V at 60 W continuous (reduced power). The default
at power-on is full power; if necessary, reduce the power as
follows.
TEST CONTROL > TEST POWER (Power) ESC
. Adjust the output voltage to the desired value with knob (6).. Connect the relay to be tested to sockets (61). Check that the
adjusted voltage does not drop as you connect the relay; else,
this would mean that T 1000 PLUS is overloaded (or that you are
connecting to a live wire). In this situation, remove the cause of
error and connect again.
1.6 AC VOLTAGE GENERATION FROM THE AUXILIARY OUTPUT
The auxiliary AC voltage is used to test relays that need voltage
and current at the meantime. In this situation, the voltage is
continuously generated; usually, it is adjusted to the nominal
8/19/2019 Bo thu ro le T1000
20/108
DOC. MIE92093 Rev. 1.34 Page 20 of 108
RANGE @50 Hz
VMAX @15 Hz
POWER @15 Hz
VMAX @33.3 Hz
POWER @33.3 Hz
V V VA@VOUT
V VA@VOUT
65 25 8 @ 22.5 V 55 35 @ 55 V
130 50 12 @ 45 V 110 35 @ 110
V
260 100 15 @ 90 V 220 35 @ 220
V
DO NOT EXCEED THE MAXIMUM VOLTAGES OF THE ABOVE
TABLE: THE OUTPUT WOULD BE DISTORTED!
. The operating mode is pre-selected as Fault: do not change it.
Do not change also the pre-selected frequency, as Locked tomains. Last, set the desired current phase angle; however, to
perform this, T 1000 PLUS must be ON, and some current must
circulate. Selections are performed as follows.
AUX VAC/VDC > Aux Vac control > Range > (Range) RET
8/19/2019 Bo thu ro le T1000
21/108
DOC. MIE92093 Rev. 1.34 Page 21 of 108
pre-fault voltage, that simulates the situation prior to fault, and
the fault voltage.
The pre-fault voltage adjustment is performed by the control
knob, while knob (20) adjusts the fault value. Voltage output
selection is automatic: pre-fault voltage with test stopped; fault
voltage with test started. The switch from a value to the other
one is performed without falling to zero. The main current or
voltage is generated at the zero crossing; the fault one isgenerated at the meantime of main voltage or current. The
selection of the reference is performed automatically, following
the selection of main output measurement. If the main DC
voltage is selected the reference is taken on the main AC voltage.
8/19/2019 Bo thu ro le T1000
22/108
DOC. MIE92093 Rev. 1.34 Page 22 of 108
AUX VAC/VDC > Aux Vac control > Frequency > Adjust >(Frequency value) ESC
The angle adjustment is performed as explained above; the
difference is that the adjustment is applied only when T 1000
PLUS is ON; with the instrument OFF, the pre-fault voltage is
normally in phase with the current. It is also possible to phase
shift the pre-fault voltage with respect to the fault voltage. This
parameter is necessary during the test of distance relays, whenphase to phase faults are simulated: as test starts, the auxiliary
voltage changes amplitude and phase with respect to the pre-
fault value.
8/19/2019 Bo thu ro le T1000
23/108
DOC. MIE92093 Rev. 1.34 Page 23 of 108
As test starts, the frequency goes to the pre-set frequency, and
from that value starts increasing or decreasing with the pre-set
ROC.
NOTE: The auxiliary AC voltage is protected by an electronic
circuit that stops the voltage generation and opens the
connection to outputs socket in case of overload (short circuit
included). In case of intervention, an alarm message is displayed.
Via the control knob the operator can reset the alarm and closethe relay to restore operation.
The auxiliary AC voltage is also protected by a thermo switch that
intervenes in case of over-heating. In case of intervention, an
alarm message is displayed.
1.7 DC VOLTAGE GENERATION FROM THE AUXILIARY OUTPUT
The second auxiliary generator can be used to supply the
auxiliary DC voltage for the relay to be tested. To this purpose,
the voltage is available at sockets (63), after pressing the push-
f
8/19/2019 Bo thu ro le T1000
24/108
DOC. MIE92093 Rev. 1.34 Page 24 of 108
relay; else, this would mean that T 1000 PLUS is overloaded (or
that you are connecting to a live wire). In this situation, if it is not
a connection error, it is possible to reduce the voltage until thevoltage does not drop: relays tolerate a wide range of DC supply
voltages.
The auxiliary DC voltage is protected by a current limiter. The
user notices the low voltage and removes the overload. The fuse
protects the case of counter-feed.
1.8 AUXILIARY CONTACTS
- The two auxiliary outputs have make and break contacts, that
close (open) at test start after the programmed delay, and open(close) as current is cut off after the STOP input is sensed.
Contacts can be used to simulate the circuit breaker state.
- Possibility to delay the auxiliary contacts switch with respect to
test start. Delay range: from 0 to 999.99 s.
DOC MIE92093 R 1 34 P 25 f 108
8/19/2019 Bo thu ro le T1000
25/108
DOC. MIE92093 Rev. 1.34 Page 25 of 108
. For both inputs, when the input is closed or with voltage an LED
turns on;
. When the relay intervenes the TRIP light turns on;. Inputs protection: if the voltage free input is selected and a
voltage is applied, no damage occurs, provided that the voltage is
within the specified limits.
. When the input is with voltage, it is possible to select the
voltage threshold. Low threshold is for voltages between 24 and
48 V; high threshold is for voltages above 100 V .
The timer offers a number of possible selections to permit many
different types of testing depending on the selection by the
operator. The following flow shows all possible selections.
DOC MIE92093 R 1 34 P 26 f 108
8/19/2019 Bo thu ro le T1000
26/108
DOC. MIE92093 Rev. 1.34 Page 26 of 108
the corresponding energy (if selected). The selection is performed
as follows:
TIMER START/STOP > STOP > External > Count > (numberof counts) ESCIf the count is selected on START, time measurement will be
performed after the set number of counts has expired: this serves
to pass the start-up of the energy meter.
Input thresholds. When the contact has voltage applied, twothresholds can be selected. The low setting applies to nominal
voltages of 24 and 48 V; the high setting to 110 V up. The
selection is performed as follows:
TIMER START/STOP > STOP > External > Clean-voltage >Voltage threshold ESC
Time can be metered as seconds or cycles (second is the default).
The selection is performed as follows:
TIMER START/STOP > Units > s or Cycles ESC
DOC MIE92093 Rev 1 34 Page 27 of 108
8/19/2019 Bo thu ro le T1000
27/108
DOC. MIE92093 Rev. 1.34 Page 27 of 108
1.10.2. First threshold trip and drop-off
The first session is finding threshold I>, that is the limit between
DOC MIE92093 Rev 1 34 Page 28 of 108
8/19/2019 Bo thu ro le T1000
28/108
DOC. MIE92093 Rev. 1.34 Page 28 of 108
1.10.3. Second threshold trip and drop-off
The second session is finding threshold I>>. The problem is thatthe test result criterion is no more to find the limit between no
trip and trip; it is instead to find the limit between two different
timings: what we have shown as t>, for currents less than I>>,
and t>> for currents more than I>>. There are many ways to
perform the test; we suggest taking advantage of the Timed
generation option, as follows.
. Start from a current more than I>; select ON+TIME, and check
for time response. Take note of the timing t>. Compute tmax as
80% of t>.
. Set the maximum test duration as tmax: the relay will not trip
until you enter the I>> zone.. Select ON+TIME, and start the test: the test goes OFF with no
message. Slowly increase the test current and repeat the tests,
until the relay trips within tmax: this is the threshold; pressing
the multi-function knob tripping values can be saved.
NOTE: this procedure applies to any multi-threshold relay,
DOC MIE92093 Rev 1 34 Page 29 of 108
8/19/2019 Bo thu ro le T1000
29/108
DOC. MIE92093 Rev. 1.34 Page 29 of 108
. Under-current relay trip delay: from ON to OFF+TIME;
. Under-current relay drop-off delay: from OFF to ON+TIME.
All these tests are performed after having pre-adjusted the
desired test current (or set of parameters).
I
t
5A) Overcurrent relay trip delay
I
Stop
FAULT
Trip delay
DOC MIE92093 Rev 1 34 Page 30 of 108
8/19/2019 Bo thu ro le T1000
30/108
DOC. MIE92093 Rev. 1.34 Page 30 of 108
. Now, press ON and pre-adjust the first set of fault parameters:
as the relay trips, don’t save test result; go OFF.
. Select ON+TIME: as the relay trips, test goes OFF; pressing themulti-function knob tripping values can be saved. The TRIP LED
(43) turns on and parameters at trip are displayed until ON or
ON+TIME are selected. Confirm save results pressing the multi-
function knob, and proceed with other test currents, until all
points to be tested are measured.
Now we can measure the drop-off timing.
. First thing, select the NC level for the relay reset contact:
. Now, press ON and pre-adjust the same set of fault parameters.
. Select OFF+TIME: as the relay resets, pressing the multi-
function knob drop-off values can be saved. Confirm save results
pressing the multi-function knob, and proceed.
With different test values, other timings can be measured.
1.12 TEST RESULTS HANDLING
Before performing a test, it is important to program the test
DOC MIE92093 Rev 1 34 Page 31 of 108
8/19/2019 Bo thu ro le T1000
31/108
DOC. MIE92093 Rev. 1.34 Page 31 of 108
The operation to input the header is the following.
After having entered, if you move the knob it will move
between: arrow up; Plant name; arrow down, Return.
If you press the arrow up or down, you will scroll through:
Plant name, Operator, Serial number, Model/manuf.,
Feeder.
Once you have reached the desired description, select it
and press: the description goes in reverse, and you can
edit it.
The editor is performed as follows. If you turn the knob, it
will reach a number of selections in the bottom, and then
the line with the alphabet letters; at the end of this, there
is a double arrow, that, if pressed, replaces letters with
digits.
The input is performed reaching for a letter with the knob,
and pressing it: the letter is copied into the description.
DOC. MIE92093 Rev. 1.34 Page 32 of 108
8/19/2019 Bo thu ro le T1000
32/108
DOC. MIE92093 Rev. 1.34 Page 32 of 108
sure to save the correct data. Save is performed both in ON mode
and in ON+TIME mode.
With the selection Manual, it is possible to save data at any time,
pressing MENU and then Yes, even if the relay did not trip. As
already explained, a threshold is verified with two tests: with a
value the relay trips, with a slightly different value the relay does
not trip. This is to be selected when you are looking for the no-
trip limit of a threshold.
Once results are saved, it is possible to review or to delete them
with the command Results > Show results. The display showsthe list of the relay serial numbers, followed by the number of
tests performed with the same header.
Pressing on the relay serial number you access a window with:
Plant name, Serial number, operator. You can: return, delete
escape. Pressing Delete, a confirmation message is displayed.
Pressing Yes, all results are deleted; pressing No, you return to
the results list.
DOC. MIE92093 Rev. 1.34 Page 33 of 108
8/19/2019 Bo thu ro le T1000
33/108
DOC. MIE92093 Rev. 1.34 Page 33 of 108
The easiest type of test is to check the settings. In this instance it
is sufficient to generate the relevant parameters (voltage,
current, angle) with values close to the settings. With two timing
tests, little below and little above the settings, it is possible to
test that they are correct, within a specified tolerance.
For instance, testing an over-current relay set at 10 A can be
performed with two delay tests: at 9.5 A (-10%) the relay should
not trip; at 10.5 A (+5%) it should trip; also the timing can be
tested.
A more complex and complete test is the control of the complete
characteristic curve of the relay. There are two types of
characteristic curves:
- Parameter vs. time: it displays the trip time as the parameter
changes. Examples are: current vs. time, for an over-current
relay; impedance vs. time for a distance relay. It is understood
that for currents less than the threshold, or for impedances
higher than the general starter, no trip occurs.
DOC. MIE92093 Rev. 1.34 Page 34 of 108
8/19/2019 Bo thu ro le T1000
34/108
g
I-t over-current relay curve
The curve means that:
. If the test current is less than I> no trip occurs;
. For current more than I> and less than I>> trip time is a
function of the test current;
. For currents more than I>> the trip time is t>>.
t
I
t>>
I> I>>
DOC. MIE92093 Rev. 1.34 Page 35 of 108
8/19/2019 Bo thu ro le T1000
35/108
g
keeping the other one constant. However, we must be careful
before executing the test.
I-V directional relay curve
For instance, in order to find the point A it is apparent that the
procedure is:
V
IImin
Vmin
A
B
DOC. MIE92093 Rev. 1.34 Page 36 of 108
8/19/2019 Bo thu ro le T1000
36/108
The area to the right is the trip zone; to the left it is the no tripzone. The test strategy should be the following:
. For points A, B, D: set the test voltage and increase the current
until the relay trips;
. For point C, set the test current and decrease the voltage until the relay trips
V
I
A
I V 0
V M I N
V N
I V N
B
C
D
DOC. MIE92093 Rev. 1.34 Page 37 of 108
8/19/2019 Bo thu ro le T1000
37/108
The area of intervention is the one within the circle with the
centre in the negative X axis. The first problem is to convert R
and X into the corresponding V, I, angle; then, the current isset at IN, and only voltage and phase are modified. The test isperformed as follows:
. For point A, set the angle at 270°, start from V=0 and increase
V until the relay trips;
. For point B, set the angle at 270°, start from V higher thanthe setting and decrease V until the relay trips;. For point C, set for V the average of A and B, start from an
angle greater than 270° and reduce it until the relay trips. In a
similar way, for D, start from an angle smaller than 270° and
increase it until the relay trips.
. For other points, you have to decide whether to take the angle
constant and change the voltage or vice versa; you should choose
the variation that is not tangent to the characteristic curve.
1.14 USE OF THE TEST SET AS A MULTIMETER
The test set can be used as a powerful multimeter, as it allows
measuring:
Voltage AC and DC;
DOC. MIE92093 Rev. 1.34 Page 38 of 108
8/19/2019 Bo thu ro le T1000
38/108
. The frequency is measured only on the voltage input: connect it
and select the F measurement.
. The measurement of the impedance or of the resistance of a
component fed by an external source is performed as follows.
.. Open the circuit, and connect the component to the
external current measurement;
. Connect the component terminals to the external voltage
measurement: this avoids errors caused by the connection
leads and by the current measurement circuit;
. Select the desired measurement (Z+ φ, or R+X);
. Close the circuit, taking care not to exceed the current
limits. The measurement does not change as soon as current
and voltage are high enough: this confirms the correct
measurement.
. For power measurements of an external source proceed as
follows... Open the circuit, and connect the component to the
external current measurement;
. Connect the component terminals to the external voltage
measurement: this avoids errors caused by the connection
leads and by the current measurement circuit. Take care not
DOC. MIE92093 Rev. 1.34 Page 39 of 108
8/19/2019 Bo thu ro le T1000
39/108
N. PARAMETER , ACINPUTS
DERIVEDFROM
FORMULA UNITS
1 ACTIVE POWER, P Iext, Vext;
φ
P = I*V*cos
(φ)
W
REACTIVE POWER, Q Iext, Vext;
φ
Q =
I*V*sin(φ)
VAr
2 APPARENT POWER, S Iext, Vext S= I*V VA
POWER FACTOR, p.f. φ p.f. = cos(φ) -3 IMPEDANCE, Z and φ Iext, Vext,
φ
Z = V/I Ohm,
°
4 ACTIVE IMPEDANCE
COMP., R
Iext, Vext;
φ
R = Z*
cos(φ)
Ohm
REACTIVE IMPEDANCE
COMP., X
Iext, Vext;
φ
X = Z*
sin(φ)
Ohm
5 FREQUENCY, F Vext - Hz
6 PASE ANGLE, IE TO V2 Φ, IE-V2;
ref. V2
- °
PASE ANGLE, VE TO V2 Φ, VE-V2;
ref. V2
- °
DOC. MIE92093 Rev. 1.34 Page 40 of 108
8/19/2019 Bo thu ro le T1000
40/108
Hz: these values are higher than those of the standard T1000
PLUS.
RANGE @50 Hz
VMAX @15 Hz
POWER @15 Hz
VMAX @33.3 Hz
POWER @33.3 Hz
V V VA@VOUT
V VA@VOUT
3 1.8 20 @ 20 A;
14 @ 10 A
3.2 40 @ 20 A;
25 @ 10 A
65 35 8 @ 35 V 65 45 @ 65 V
130 70 14 @ 70 V 130 35 @ 130
V
260 140 30 @ 140
V
260 35 @ 260
V
1.16 FILTERING HEAVY BURDEN DISTORTION WITH THE FT1000 OPTION
Some very old electromechanical relays may have very inductive
loads, which change in value during the test. As the test set
DOC. MIE92093 Rev. 1.34 Page 41 of 108
8/19/2019 Bo thu ro le T1000
41/108
Next, all you have to do is to connect FT1000 in series to the
T1000 selected output: the FT1000 range shall be the same or
greater than the one of T1000.
DOC. MIE92093 Rev. 1.34 Page 42 of 108
8/19/2019 Bo thu ro le T1000
42/108
2 TEST SET AND POP-UP MENU
2.1 THE FRONT PANEL
DOC. MIE92093 Rev. 1.34 Page 43 of 108
8/19/2019 Bo thu ro le T1000
43/108
The following list includes the key components inside T 1000
PLUS; see the schematic on last page.
1) Main supply fuse, rated T10A, incorporated in the supply
socket.
2) Power-on switch.
6) Main outputs adjustment.
8) Earth socket.
13) Output sockets for main current output.19) Auxiliary DC voltage fuse, F2A.
20) Adjustment of auxiliary AC voltage output.
21) Adjustment of auxiliary DC voltage output (not available on
the model TD1000 – 15 Hz).
22) MENU control knob, with switch.
23) Display.24) Resistors set.
31) Internal START selection light.
32) Normal Open START selection light.
33) Normal Closed START selection light.
DOC. MIE92093 Rev. 1.34 Page 44 of 108
8/19/2019 Bo thu ro le T1000
44/108
52) OFF + TIME light: current is removed and time metered until
STOP is detected.
53) Main AC voltage selection light.
54) Main DC voltage selection light.
55 and 56) START and STOP push-buttons.
57) Push-button for the selection of main output.
60) Main AC voltage safety sockets.
61) Main DC voltage safety sockets.
62) Auxiliary AC voltage (also current on TD1000) safety socketsand light: ON = output available.
63) Auxiliary DC voltage safety sockets and light: ON = output
available.
64) Sockets for the connection to the external Start input.
65) Sockets for the connection to the Stop input.
66) Auxiliary outputs Normal Open and Normal Closed contacts.67) External current meter safety sockets.
68) External voltage meter safety sockets.
69) Auxiliary DC voltage ON-OFF switch.
70) Auxiliary AC voltage ON-OFF switch.
71) USB interface connector.
DOC. MIE92093 Rev. 1.34 Page 45 of 108
8/19/2019 Bo thu ro le T1000
45/108
After power-on, the auxiliary AC voltage is available at sockets
(62) after pressing the push-button (70), and can be adjusted
with the knob (20). Also the auxiliary DC voltage is available atsockets (63) after pressing the push-button (69), and can be
adjusted with the knob (21).
When the menu is accessed, the measurements are displayed
without the headings. If some further measurement is selected
(external measurements, power..) they are displayed below themenu, and only while the menu is not accessed.
2.3 THE POP-UP MENU
The following is the list of features that are menu selected. The
menu is operated by means of the control knob marked MENU,
that incorporates a switch. The menu is entered pressing the
knob and selecting the item moving the knob. Once the item has
bee found and programmed, pressing the arrow the menu moves
back of one step, so that other programming can be performed;
else selecting ESC the menu returns to the main window
DOC. MIE92093 Rev. 1.34 Page 46 of 108
8/19/2019 Bo thu ro le T1000
46/108
The flux diagram of menu selections can be found in Appendix 1.
LEVEL1 LEVEL 2 LEVEL3
LEV. 4 FUNCTION
TEST
CONTROL
Test
mode
Normal
(default)
Measures the time
delay from START
(internal, external) to
STOP (internal,
external).
Trip + pulse
time
Measures the time
delay from START
(internal, external) to
STOP (internal,
external), and the
duration of STOP.
Reclose
mode
TD;
No
Two delays are
measured: fault to
DOC. MIE92093 Rev. 1.34 Page 47 of 108
8/19/2019 Bo thu ro le T1000
47/108
External Generation starts
upon reception of the
START input: this
allows synchronising
T 1000 PLUS. When
selected, the fault is
injected as soon as
the selected
condition on START
input is met.Timed Max
time
Generation lasts for
the pre-set time
duration. Max time
999 s.
OFF
delay
T delay The main output OFF
is delayed by the setamount of time or
cycles.
Output
power
300 VA
(default) – 60
VA
Selection of full (300
VA) or reduced (60
VA) power
DOC. MIE92093 Rev. 1.34 Page 48 of 108
8/19/2019 Bo thu ro le T1000
48/108
TIMERSTART/STOP
Start INT (default) Timer starts when ONor ON+TIME are
activated and outputs
generated.
EXT NO-NC-
EDGE
After ON or ON+TIME,
timer starts on the
external input. External
START input Normally
Open, or Normally
Closed, or Both(EDGE).
CLEAN-
24 V – 80
V
After ON or ON+TIME,
timer starts on the
external input. External
START input without or
with voltage. If withvoltage, two voltage
thresholds are
available: 24 or 80 V.
COUNT Timer enters the
counting mode; it is
DOC. MIE92093 Rev. 1.34 Page 49 of 108
8/19/2019 Bo thu ro le T1000
49/108
CLEAN-
24 V – 80
V
Timer stops when the
STOP input is detected.
External STOP input
without or withvoltage. If with
voltage, two voltage
thresholds are
available: 24 or 80 V.
COUNT Timer enters the
counting mode; it ispossible to program
the number N of
transitions to be
detected. After ON or
ON+TIME, the time
from the first validinput to input N+1 is
measured; the
corresponding energy
can be read on the
display.
DOC. MIE92093 Rev. 1.34 Page 50 of 108
8/19/2019 Bo thu ro le T1000
50/108
LEVEL1
LEV.2
LEV.3
LEVEL4
LEVEL 5 FUNCTION
AUX
VAC/VDC
Aux
Vaccontrol
Range 65 (default) ;
130 ; 260 V.
Mode Fault (default) The auxiliary
AC voltage is
adjusted by
the dedicated
knob, and is
available afterpressing the
ON-OFF
pushbutton. If
the auxiliary
voltage should
be appliedalong with the
main current
or voltage, go
to next
selection
DOC. MIE92093 Rev. 1.34 Page 51 of 108
8/19/2019 Bo thu ro le T1000
51/108
Prefault
+ Fault
Prefault
Amplitud
e
Sets the pre-
fault auxiliary
AC voltage
amplitude.Entering this
selection in
OFF mode, the
pre-fault
voltage is
generated anddisplayed, and
adjusted by
the multi-
function knob.
NOTE: the
fault voltage isgenerated
pressing ON or
ON+TIME, and
it is adjusted
as usual by the
DOC. MIE92093 Rev. 1.34 Page 52 of 108
8/19/2019 Bo thu ro le T1000
52/108
Prefault
duration
Sets the
duration of the
pre-fault
auxiliaryvoltage. When
ON or
ON+TIME are
pressed, the
pre-fault will
be generatedat the mains
frequency for
the selected
duration; then
the fault
voltage isgenerated, at
the
programmed
frequency.
Prefault The prefault
DOC. MIE92093 Rev. 1.34 Page 53 of 108
8/19/2019 Bo thu ro le T1000
53/108
Adjust
freq
40-
500.00
0
The frequency
of the auxiliary
voltage may be
programmed.Frequency
changes at test
start; output
voltage does
not change in
amplitude.Adjust
r.o.c.: 0.01..
9.99
Hz/s
The frequency
ramps at the
programmed
rate of
Change. The
startingfrequency can
be the mains
or the value
set by adjust
freq.
DOC. MIE92093 Rev. 1.34 Page 54 of 108
8/19/2019 Bo thu ro le T1000
54/108
Adjust phase Vaux
- mains
The fault
auxiliary
voltage can be
phase shiftedwith respect to
the mains. The
measured
angle is
displayed. Test
must be ON;for a correct
angle
measurement,
the auxiliary
voltage must
be more than20% of the
range. Phase is
adjusted by
the
multifunction
DOC. MIE92093 Rev. 1.34 Page 55 of 108
8/19/2019 Bo thu ro le T1000
55/108
Adjust phase Vaux
– I main
The fault
auxiliary
voltage can be
phase shiftedwith respect to
the main
current. The
measured
angle is
displayed. Testmust be ON;
for a correct
angle
measurement,
current and
voltage mustbe more than
20% of the
range. Phase is
adjusted by
the
DOC. MIE92093 Rev. 1.34 Page 56 of 108
8/19/2019 Bo thu ro le T1000
56/108
Adjust phase Vaux
– V main
The fault
auxiliary
voltage can be
phase shiftedwith respect to
the main
voltage. The
measured
angle is
displayed. Testmust be ON;
for a correct
angle
measurement,
both voltages
must be morethan 20% of
the range.
Phase is
adjusted by
the
DOC. MIE92093 Rev. 1.34 Page 57 of 108
8/19/2019 Bo thu ro le T1000
57/108
LEVEL1 LEVEL 2 LEVEL 3 LEVEL 4 FUNCTION
METERS Internal Units of I Normal If selected,current
values aredisplayed in
A.
I/IN I
If selected,
displayed
values are
defined asI/IN, that
can be
defined.
Units of V Normal If selected,
voltage
values aredisplayed in
V.
V/VN If selected,
displayed
values are
DOC. MIE92093 Rev. 1.34 Page 58 of 108
8/19/2019 Bo thu ro le T1000
58/108
10A – 20
mA
Selects the
current
input socket
Waveform If selected,the current
waveform is
displayed
External V
Enabled AC
(default) -
DC
With
selection AC
the meterperforms
the true rms
measureme
nt; with
selection
DC, themeasureme
nt is
performed
on the
average
DOC. MIE92093 Rev. 1.34 Page 59 of 108
8/19/2019 Bo thu ro le T1000
59/108
LEVEL1 LEVEL 2 LEVEL 3 FUNCTION
METERS
(continued)
Other
internal
None (default) No extra
measurementdisplayed
Active power P; W
Reactive power Q; VAr
Impedance module Z, Ohm
Impedance argument φ, °
Active impedancecomponent
R, Ohm
Reactive impedance
component
X, Ohm
Apparent power S; VAPower factor p.f. = cos(φ V-I)
Active energy (AC) Ea; Wh
Reactive energy (AC) Er; VArh
Other
externa
None (default) No extra
measurement
DOC. MIE92093 Rev. 1.34 Page 60 of 108
8/19/2019 Bo thu ro le T1000
60/108
Note: measurements marked AC apply only if both inputs are
selected as alternate current.
LEVEL1 LEVEL 2 LEVEL 3 LEVEL4
FUNCTION
RESULTS Test header Groups results
Show results Display result
Delete Selectedresult(s)
All resultsCONFIGU-
RATION
Settings Save to
address
1..10 Saves current
settings to X
Restore
address
1..10 Restores settings
from X
Restore
default
1..10 Restores default
settings
Language UK, FR, SP, PT,GE, IT
Select the desired
language
Display Speed Slow The displayed
value is refreshed
every 1000 ms
DOC. MIE92093 Rev. 1.34 Page 61 of 108
8/19/2019 Bo thu ro le T1000
61/108
3 WHAT’S INSIDE?
3.1 PHYSICAL DESCRIPTION
The test set is contained in an housing, to which it is fixed by
means of nine screws that are located below it: see the following
picture.
DOC. MIE92093 Rev. 1.34 Page 62 of 108
8/19/2019 Bo thu ro le T1000
62/108
DOC. MIE92093 Rev. 1.34 Page 63 of 108
16) C b d d PWA11401
8/19/2019 Bo thu ro le T1000
63/108
16) Converter board code PWA11401.
17) Front panel board; code PWA11398.
24) Resistors set.
26) MISU T 1000 PLUS board code PWA11402.27) Protection fuses board, code PWA11416.
The arrangement is shown in the figure and pictures below.
DOC. MIE92093 Rev. 1.34 Page 64 of 108
8/19/2019 Bo thu ro le T1000
64/108
DOC. MIE92093 Rev. 1.34 Page 65 of 108
Thei location is sho n in the d a ing belo Ca ds a e kept in
8/19/2019 Bo thu ro le T1000
65/108
Their location is shown in the drawing below. Cards are kept in
place by the piece of aluminium sheet on the right, and also by
the threaded bar between the boards. If a board is failing, it is
necessary to remove the two screws as shown, and to un-tightenthe nut of the threaded bar, as shown; in case some component
touches it, it is necessary to remove it.
DOC. MIE92093 Rev. 1.34 Page 66 of 108
VOLTAGE POWER PURPOSE GOES TO
8/19/2019 Bo thu ro le T1000
66/108
VOLTAGEV
POWERVA
PURPOSE GOES TO
150 120 Supply of auxiliary DC voltage
module YWA11395 (9)
PWA11395
J800-1; 411.5 3 Auxiliary supply for auxiliary
DC voltage module
YWA11395
PWA11395
J800-2, 3
50 60 Low power test supply 2 WAY
CONN.
36 x 2 35 x 2 Power supply of auxiliary ACvoltage board PWA11396 (10)
PWA11396J1-1; 2; 3
15.2 x 2 10 x 2 General auxiliary ± 15 V
supply for all analog circuits
PWA11399
JP 10
12 10 General auxiliary + 5 V
supply for all digital circuits
PWA11399
JP 8
10 10 General auxiliary + 12 Vunregulated supply (relays, ..)
PWA11399JP 9
4.5 7 Unregulated + 5 V supply for
the display back-light
PWA11399
JP 7
3 2 2 Auxiliary transformer XTF10245 (4)
DOC. MIE92093 Rev. 1.34 Page 67 of 108
10 1 Positive voltage for the PWA11396
8/19/2019 Bo thu ro le T1000
67/108
10 1 Positive voltage for the
buffer of AC voltage
board PWA11396 (10)
PWA11396
J2-4, J1-6
10 1 Negative voltage for thebuffer of AC voltage
board PWA11396 (10)
PWA11396J1- 4, 5
11.5 x 2 1.5 x 2 I measurement circuit
supply
PWA11398
J812-1, 2,
3
11.5 x 2 1.5 x 2 V measurement circuitsupply
PWA11398J812-4, 5,
6
The following drawing shows the back panel board (11) and the
JP points, where many wires are soldered.
DOC. MIE92093 Rev. 1.34 Page 68 of 108
8/19/2019 Bo thu ro le T1000
68/108
3.2.3 Main output transformer, XTF10345 (5)
The main output transformer (5) has the following secondary
windings. For connections, see the schematic at the end of this
manual.
VOLTAGE
V
POWER
VA
PURPOSE
225 +
296
125 Main DC voltage
Main AC voltage (same common)
90+
25+
10
400
300
300
10 A output (60 s maximum)
40 A output (60 s maximum)
100 A output (60 s maximum)
(same common)
3.2.4 Main front board PWA11398 (17)
The board includes many different circuits:
DOC. MIE92093 Rev. 1.34 Page 69 of 108
All circuits have: gain selections; high accuracy amplifiers;
8/19/2019 Bo thu ro le T1000
69/108
All circuits have: gain selections; high accuracy amplifiers;
high accuracy isolated op amps.
Analog outputs are taken to CONV1000, for the ADC
conversion.
3.2.6 CONV T1000 board PWA11401 (16)
TASK 1: to convert all analog measurement signals (the
above + main I + main V AC + main V DC + auxiliary V AC)
into digital signals. This is performed by two 12-bit, 4channels each parallel ADC converters.
TASK 2: to generate a squared waveform in phase with the
mains input, and to square the AC current and voltage signals
for the phase meter. Three circuits with amplifiers, limiters,
comparators perform this task.
TASK 3: to generate a sinusoidal waveform, with controlledfrequency and amplitude, that will be passed to the auxiliary
AC voltage amplifier (10). This is made by the local micro DSP
processor that generates the inputs for two DAC’s, that
control the amplitude and the waveform, at 10 kHz.
On the board is located a set of 8 switches; their meaning is
DOC. MIE92093 Rev. 1.34 Page 70 of 108
3.2.7 INTE ON-OFF T 1000 board PWA11400 (7)
8/19/2019 Bo thu ro le T1000
70/108
3.2.7 INTE ON OFF T 1000 board PWA11400 (7)
TASK 1: to detect the START and STOP inputs closed – open
situation via two isolated constant current generator circuits,with wet/dry selection and opto-isolated logic output.
TASK 2: to drive the ON-OFF of the test set. There are two
SCR’s pairs (one per phase) in opposing mounting, mounted
on heat sinks. SCR characteristics: 600 V AC; 20 A steady;
200 A peak.
TASK 3: diagnostic circuits of the main auxiliary supplies.
3.2.8 MICR T 1000 board PWA41300 (15)
The microprocessor board is the same as the one of the DRTS
family, but without the two PLA’s. It is controlling the test set
operation, test and results handling and the communication withthe PC, but not the AC waveform generation, that is controlled by
a dedicated slave microprocessor.
3.2.9 AP-50 AC Voltage board PWA11396 (10)
DOC. MIE92093 Rev. 1.34 Page 71 of 108
By the side of the boards support is mounted a board with a set
8/19/2019 Bo thu ro le T1000
71/108
By the side of the boards support is mounted a board with a set
of protection fuses. They protect the following modules:
. Auxiliary DC voltage supply: timed 0.25 A;
. Display backlight: timed 1.6 A;
. Internal supply + 15 V: timed 1 A;
. Internal supply - 15 V: timed 1 A;
. Internal supply + 5 V: timed 0.8 A;
. Internal supply + 12 V: timed 1 A.
The position of fuses is shown in the picture below.
The first one protects the auxiliary supply: if it is blown, there is
DOC. MIE92093 Rev. 1.34 Page 72 of 108
8/19/2019 Bo thu ro le T1000
72/108
J812: MAIN BOARD (17)
PIN 1 2 3 4 5 6VOLTAGE 11,5 V REF. (1-3) 11,5 V 11,5 V REF. (4-6) 11,5 V
TRANSFO (4) (4) (4) (4) (4) (4)
J815: MAIN BOARD (17)
PIN 1 2VOLTAGE 8 V REF. (1)
TRANSFO (4) -
J817: MAIN BOARD (17)
PIN 1 2VOLTAGE 7 V REF. (1)
TRANSFO (4) (4)
J820: MAIN BOARD (17)
DOC. MIE92093 Rev. 1.34 Page 73 of 108
8/19/2019 Bo thu ro le T1000
73/108
4 THE HELL, IT DOESN’T WORK
4.1 INTRODUCTION
Sometimes, when my ears whistle, I wonder if it is because of
some of my customers being angry at us because the test set
doesn’t work: according to Murphy’s law, when it was most
necessary. We at ISA do our best efforts to filter the so-called
infant mortality of electronic components prior to delivery of allour test sets; and this after extensive testing of prototypes and
pre-production units.
Yet, sometimes faults occur, because everything dies, including
electronic components; so, please, before shooting at us, see if
the following instructions can serve you to fix the problem. If not,e-mail us the problem, not forgetting to mention the unit’s
serial number: our business is to minimize your downtime. Mye-mail address is:
DOC. MIE92093 Rev. 1.34 Page 74 of 108
8/19/2019 Bo thu ro le T1000
74/108
4.2 ERROR MESSAGES
The test set performs a number of tests at power-on and during
the generation. The following table lists all the messages, and thecorrective action.
A) TESTS AT POWER-ON (and runtime)
ERROR MESSAGE CONSEQUENCE CORRECTIVE
ACTION+ 15 V supply failure If the error is not
confirmed it is
possible to continue;
else, the test cannot
proceed
(NOTE 1)
Try some power
on – off; if
persists, three
steps:
. Check the
fuses;Try to replace
e CONV board;
. Return the
test set.
15 V supply failure If the error is not Try some power
DOC. MIE92093 Rev. 1.34 Page 75 of 108
8/19/2019 Bo thu ro le T1000
75/108
B) RUNTIME TESTS
ERRORMESSAGE
CONSEQUENCE CORRECTIVEACTION
60 VA IAC supply
time
The test lasted
too long; tests
are blocked for
the specified
duration
Wait until the
message disappears
300 VA IAC
supply time
The test lasted
too long; tests
are blocked for
the specified
duration
Wait until the
message disappears
IAC while VDCsupplied
Generation isstopped
The test set issensing a burden
both on main IAC
and VAC or VDC,
what is forbidden.
Remove one of the
DOC. MIE92093 Rev. 1.34 Page 76 of 108
disappears, the
8/19/2019 Bo thu ro le T1000
76/108
test set informs
you about the
residual timeOVERTEMP
POWER
TRANSFORMER
Generation is
stopped
(NOTE 1)
The main
transformer
temperature is too
high because of
heavy loads or very
long test duration:wait until it cools
down. If it does not
disappear, see the
text.
OVERTEMP
SCR’S HEAT
Generation is
stopped(NOTE 1)
The temperature of
the SCR that drivesthe test is too high
because of heavy
loads or very long
test duration: wait
until it cools down
DOC. MIE92093 Rev. 1.34 Page 77 of 108
The following table summarizes main faults, cause of fault and
8/19/2019 Bo thu ro le T1000
77/108
correction. When in the correction you find “see text”, please
proceed with the following paragraphs.
SYMPTOM POSSIBLE CAUSE CORRECTION
Problems after
transport
Heavy shock Open T 1000 PLUS
and check for
loose boards or
connections
At power-on doesnot turn on
Mains supply fuseopen
Other causes
See text
The variable
transformer gets
very hot as soon
as the test set ispowered-on
The INTE board is
faulty
Replace INTE
After the general
over-temperature
alarm message it
does not turn on
The power
transformer was
over-heated
Wait at least 30
minutes before
trying again: it
needs time to cool
DOC. MIE92093 Rev. 1.34 Page 78 of 108
Measurements are The microprocessor Go to the
8/19/2019 Bo thu ro le T1000
78/108
completely false has lost its
correction factors
calibration
procedure and
repeat it.The display is dark Protection fuse
blown
See text
Unstable auxiliary
AC voltage
measurement.
Fault of AC voltage
generation circuit
See text
The TRIP input isnot detected
Damaged INTE ON-OFF
See text
Over-load alarm
on the auxiliary AC
voltage cannot be
restored; AC
voltage cannot begenerated.
Fault of AC voltage
amplifier.
Contact your agent
for support,
detailing:
. test set number;
. how did it occur
A knob
(adjustment,
multi-function
wheel) does not
Friction against the
front panel
. Remove the
plastic (blue)
protection on the
front of the knob:
DOC. MIE92093 Rev. 1.34 Page 79 of 108
4.3.1 Auxiliary supplies
8/19/2019 Bo thu ro le T1000
79/108
On the edge of the CONV board are mounted a number of ring-
shaped test points. They carry the key auxiliary supplies, whichoperate the test set. The arrangement of the test points is the
following.
If any of these voltages is missing, the test set cannot operate: it
is necessary to find out if it is a problem of blown fuse, or repair
the auxiliary voltage circuit. If the main auxiliary transformer (3)
is damaged, it can be replaced with the following procedure.
The replacement transformer comes cabled with all crimped
connectors, in order to ease the replacement. There are eight
remaining wires that are to be soldered directly to the small fuse
board. The two transformers are perfectly identical: wires come
DOC. MIE92093 Rev. 1.34 Page 80 of 108
. three connectors from the DC voltage generator: two bigger,
hit th f t th l fl t bl
8/19/2019 Bo thu ro le T1000
80/108
white, one on the front, one on the rear, plus one flat cable;
. Five connectors from the AC voltage amplifier: four white,
mounted on top of the board, plus a flat cable.
After this, power-on, and verify that the display operates, and
that the LED’s on the front panel turn on with the default values.
If so, re-insert the modules one after the other, in order to detect
which one is faulty.
In case of DC voltage generator, see here below what else to do;
in case of the AC voltage amplifier, it should be replaced.
4.4 AUXILIARY DC VOLTAGE FAULT
If the output voltage cannot be adjusted, then the fault can belocated in the adjustment potentiometer. In this instance, the
behaviour is the following:
- Select the 130 V range: the output is fixed at about 10 V;
- Select the 240 V range: the output is fixed at about 20 V.
DOC. MIE92093 Rev. 1.34 Page 81 of 108
4 wires with
8/19/2019 Bo thu ro le T1000
81/108
If the potentiometer was not the problem and fuse (19) is OK, it
is possible that the fuse on the fuses board is blown, or that one
of the fuses mounted on the board has blown up. In this instance,
proceed as follows.
Open the test set as explained above and locate the fuse on
the same colour
4 wires withdifferent
colours:they comefrom thetransformer
DOC. MIE92093 Rev. 1.34 Page 82 of 108
8/19/2019 Bo thu ro le T1000
82/108
The last test is to remove the connector J800 coming from the big
F1F 3.15 A
F2F 2 A
DOC. MIE92093 Rev. 1.34 Page 83 of 108
4 5 AUXILIARY AC VOLTAGE FAULT
8/19/2019 Bo thu ro le T1000
83/108
4.5 AUXILIARY AC VOLTAGE FAULT
Possible modes for AC voltage fault are:. Over-load message at power-on, that cannot be re-set;
. Over-load message even with a minimum load;
. No AC voltage output.
In such instances, the most likely cause of fault is the amplifier
(10), PWA11396. You should open the test set, disconnect thefive connectors, remove the amplifier by unscrewing the four
screws below it, replace with the new one and verify that the test
set is operational. In order to be able to remove the amplifier,
first remove the DC voltage module (two screws), so that you can
take it away moving it to the left.
When fitting back the connectors, cables are short or with
different pin numbers, so that they cannot be exchanged, unless
for two 6-way connectors towards the bottom of the test set. The
correct location is sketched below (see the picture above)
DOC. MIE92093 Rev. 1.34 Page 84 of 108
PIN 1
8/19/2019 Bo thu ro le T1000
84/108
. Verify the signals as summarized in the following table.
PIN 1 2 3 4 5 6 7
SIGNAL Extmeas
80 V
0 Vin 0 Vin0-2 V
AC
Rangesel
H = 260
+ 12 V Extmeas
10 V
PIN 2
DOC. MIE92093 Rev. 1.34 Page 85 of 108
follow the instructions above for the opening of T 1000 PLUS and
board replacement
8/19/2019 Bo thu ro le T1000
85/108
board replacement.
4.7 DOES NOT MEASURE THE MAIN CURRENT
Remove T 1000 PLUS from the container. Just below the output
sockets there are two yellow wires going to the metering current
transformer. These yellow wires are made of a single enameled
wire coming from the secondary of the measurement
transformer: it is possible that they broke, and so you loose themeasurement. The fixing is easy: just solder the wires, taking
care to peel the enamel so that it can be soldered.
If this is not the cause of the problem, further tests:
. On the main board, close to the point where the transformer is
soldered, is located the resistor R71, rated 1 Ohm: verify that it iscorrectly soldered.
. Generate 1 A on the 10 A output, and measure the voltage
across the 1 Ohm resistor: you should measure 50 mV
(Transformer ratio 200//1; 10 turns make the ratio 20//1).
The voltage drop across the shunt is taken to the CONV board
DOC. MIE92093 Rev. 1.34 Page 86 of 108
8/19/2019 Bo thu ro le T1000
86/108
DOC. MIE92093 Rev. 1.34 Page 87 of 108
8/19/2019 Bo thu ro le T1000
87/108
. Verify the voltages on the test points of the CONV board, as
explained above. If some voltage is missing, then the auxiliary
transformer should be replaced.
. The display is connected to the main front board via a number
of pins, located in the center of the display: verify that there is no
DOC. MIE92093 Rev. 1.34 Page 88 of 108
4.9 THE AC VOLTAGE MEASUREMENT IS NOT STABLE
8/19/2019 Bo thu ro le T1000
88/108
4.9 THE AC VOLTAGE MEASUREMENT IS NOT STABLE
First of all, check that there is no unplugged connector or brokenwire. Next, it is necessary to understand if the problem is in the
measurement or if the output is actually unstable. To this
purpose, connect the output to an AC voltage meter and verify
the reading. If it is unstable as well, the problem is in the
amplifier; otherwise, it is in the measurement circuit.
In the first instance, amplifier, we have to verify if the problem
comes from the adjustment potentiometer. To this purpose,
proceed as follows:
. Go to the menu and select PREFAULT + FAULT;
. In the PREFAULT mode, the output voltage is adjusted by the
multi-function knob, and not by the potentiometer: please verifythe output. If it is stable, the problem is located in the
adjustment knob. If it is unstable, it can be located on the AP/50
amplifier, or on the CONV board. The problem when replacing
CONV is that, as it hosts the measurement circuits, after
replacing it it is necessary to repeat the calibration It is up to
DOC. MIE92093 Rev. 1.34 Page 89 of 108
contact closes, a current of about 10 mA flows though it and
detects the contact status. If with this selection the closed contact
8/19/2019 Bo thu ro le T1000
89/108
is not detected, and 20 V are not applied, the fault is located in
the INTE ON-OFF board (7), that is located in the boards pack.The replacement is very fast: just follow the instructions above
for the opening of T 1000 PLUS and board replacement.
If the replacement of the INTE ON-OFF board is not solving the
problem, check the following.
. There are two connectors on the front board: they carry theSTART and STOP inputs. Check that they are OK.
DOC. MIE92093 Rev. 1.34 Page 90 of 108
8/19/2019 Bo thu ro le T1000
90/108
. Last, on the test points shown above as STOP SUPPLY andSTART SUPPLY are soldered the wires that supply the START and
STOP circuits for the voltage free selection, and that come from
the auxiliary transformer located below the boards: if a voltage is
missing, the transformer should be replaced.
DOC. MIE92093 Rev. 1.34 Page 91 of 108
- Remove (or unlock a little) the metal bar that fixes the two
aluminium columns.
8/19/2019 Bo thu ro le T1000
91/108
- Remove the two connectors placed on the INTE board.
- Remove the INTE board, and then the pack MICRO + CONV.- Open the pack MICRO + CONV.
- Change the position of the mini-dip switch N. 8 on the CONV
board (it is OFF; it must be set ON).
- Insert again all the boards (and the INTE connectors too).
- Turn on the test set.
- At this point , the instrument should be connect to your PC.Execute the firmware download.
Verify that the new firmware version appears; if yes, you have
to turn off and set the dipswitch N. 8 to OFF (as it was initially).
4.12 THE ENCODER IS BROKEN
In this instance, it is necessary to have some skill and patience.
The procedure is the following.
. During the time, we have used three different type of encoder
mounting; they are:
1 The front-end printed circuit board does not allow to
DOC. MIE92093 Rev. 1.34 Page 92 of 108
. Unsolder the first wire, and solder it to the new encoder, in the
same position: with this procedure you are sure not to exchange
8/19/2019 Bo thu ro le T1000
92/108
wires.
. At the end of soldering, mount back the new encoder, power-onand check that it is correctly operational. After this, complete the
mounting of the test set.
4.13 THE THERMAL ALARM DOES NOT DISAPPEAR
The thermal alarm is given by either of two thermal switches putin series: one is located on the main transformer; the other one is
located on the AP-50 amplifier. One of them is faulty.
In order to understand which one is faulty, proceed as follows:
. Dismount the AP-50 amplifier (four screws from below), and lift
it enough to reach for the thermal sensor: it ends with two wires,that go to a connector.
. Disconnect the connector, and perform a temporary short circuit
on the mating connector.
. Power-on. If the error signal disappears, the fault is on the AP-
50 sensor (unless AP-50 is actually hot); else the fault is on the
DOC. MIE92093 Rev. 1.34 Page 93 of 108
8/19/2019 Bo thu ro le T1000
93/108
. The fuse to the right protects the auxiliary contact no. 1.Replace the fuse and verify again.
. If the fuse is not the problem, it is possible, even if quite
difficult, to unsolder the relay and to replace it.
4.15 THE FAULT CANNOT BE FIXED
If the fault is too hard to be fixed, you have to deliver T 1000
PLUS back to your agent. We have encountered problems caused
by a poor packing of instruments that have been delivered us for
calibration or repair. In order to avoid such inconveniences,
please apply the following procedure
DOC. MIE92093 Rev. 1.34 Page 94 of 108
INSTRUMENT RETURN FORM
8/19/2019 Bo thu ro le T1000
94/108
DATE ________________________________________AGENT _______________________________________COUNTRY _____________________________________
TYPE OF INSTRUMENT __________________________SERIAL NO. ___________________________________
INSTRUMENT RETURNED FOR:CALIBRATION ____REPAIR ____
In case of repair, please specify the following.
DATE OF FAULT _________________________________REPORTED BY E-MAIL, PHONE ______________________
DOC. MIE92093 Rev. 1.34 Page 95 of 108
HOW DID IT OCCUR _______________________________________________
8/19/2019 Bo thu ro le T1000
95/108
_______________________________________________
_______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________
LOCAL ANALYSIS OR ATTEMPTS TO REPAIR _______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________ _______________________________________________
DOC. MIE92093 Rev. 1.34 Page 96 of 108
4.16 CALIBRATION
8/19/2019 Bo thu ro le T1000
96/108
4.16.1 Introduction
T 1000 PLUS does not need to be calibrated, as metering circuits
employ high stability components.
It is suggested to check the unit every 2 years, by comparing T
1000 PLUS measurements to external meters. Tests should beperformed with an high accuracy multi-meter, that shouldguarantee a maximum AC measurement error of 0.1%, both for
voltage and current. Besides, as such multi-meters do not have
current ranges greater than 2 A, for the test of the high current
ranges it is necessary a class 0.1 measurement Current
Transformer. The adoption of lower-class instruments may causefalse interventions, that introduce errors into the test set. . Last,
as internal generators follow the mains, it should be stableenough to allow for a stable generation.
At the end of the test if deviations are not acceptable it is
DOC. MIE92093 Rev. 1.34 Page 97 of 108
8/19/2019 Bo thu ro le T1000
97/108
4.16.3 T 1000 PLUS output calibration
Calibrations are divided between external measurements and
internal generators. Starting from an internal generator, for
instance Main IAC, the following window is opened.
DOC. MIE92093 Rev. 1.34 Page 98 of 108
8/19/2019 Bo thu ro le T1000
98/108
. The first thing is the off-set calibration: to this purpose, remove
the connection to the meter, then select RESET: as you click on
it, the square dot to the left side turns white:
. Now, press SET: the square dot turns black, and the calibration
is done.
. On the upper part of the screen it is displayed the nominal
current to be used for the calibration of the selected range: in our
instance it is 1 A To the right there are two adjustment
DOC. MIE92093 Rev. 1.34 Page 99 of 108
. Next is the calibration of the AC voltage output: the window is
the following.
8/19/2019 Bo thu ro le T1000
99/108
.
. Here there are four ranges to calibrate. The procedure is the
same as above, but the off-set is calibrated by putting a short
circuit on the output.
. The main DC voltage output is similar to the above. The
auxiliary AC voltage output calibration opens the following screen.
DOC. MIE92093 Rev. 1.34 Page 100 of108
Now you can proceed with the external measurements
calibration. For this operation, IT IS NECESSARY TO HAVE AN
EXTERNAL SOURCE SUCH AS A DRTS TEST SET: T1000 ittself
8/19/2019 Bo thu ro le T1000
100/108
EXTERNAL SOURCE, SUCH AS A DRTS TEST SET: T1000 ittself
cannot be used to source the inputs.
. The window for the external IAC measurement is the following
one.
. NOTE: the first two calibrations will be performed on the 25 mA
input; the other two on the 10 A input. Also here, first calibrate
the offset (open circuit, and then the gain, inputting a currentclose to the one displayed.
. Calibrations are divided in two: AC calibration and DC
calibration. The following is the widow for the 600 V input.
DOC. MIE92093 Rev. 1.34 Page 101 of108
8/19/2019 Bo thu ro le T1000
101/108
1) Angle Auxiliary AC Voltage (reference) – Main AC
current.
Once the selection is performed, the following window is opened.
The calibration has to be performed for each voltage and current
range: nine calibrations in all. Connect the auxiliary AC voltage
output to input 1 of the reference phase meter, and the main
current output to input 2 of the reference phase meter. Take
DOC. MIE92093 Rev. 1.34 Page 102 of108
A sockets: the auxiliary AC voltage will be the same for all
ranges.
8/19/2019 Bo thu ro le T1000
102/108
2) Angle Auxiliary AC Voltage (reference) – Main Voltage.Once the selection is performed, the following window is opened.
Connect the auxiliary AC voltage output to input 1 of the
reference phase meter, and the main AC voltage output to input
2 of the reference phase meter. Take care to connect theT1000 black sockets to the negative inputs of the phasemeter.
Both voltage outputs are adjusted at 57 V. on the 62.5 V range,
and the main voltage output, The adjustment procedure is the
same described above.
DOC. MIE92093 Rev. 1.34 Page 103 of108
resistor set. Press the key >, and adjust 1 A for the first
calibration, and 5 A for the second one. The procedure is the
same as above
8/19/2019 Bo thu ro le T1000
103/108
same as above.
4) Angle Auxiliary AC Voltage (reference) – ExternalVoltage.
Once the selection is performed, the following window is opened.
Connect the auxiliary AC voltage output to input 1 of the
reference phase meter, and the external AC current input to
input 2 of the reference phase meter. Take care to connect theT1000 black sockets to the negative inputs of the phasemeter.
DOC. MIE92093 Rev. 1.34 Page 104 of108
8/19/2019 Bo thu ro le T1000
104/108
With this connection, the voltage to VEXT is about 10 V when the
input is 65 V: this is to be used for the angle calibration of the 20
common
DOC. MIE92093 Rev. 1.34 Page 105 of108
APPENDIX 1 SPARE PARTS LIST
8/19/2019 Bo thu ro le T1000
105/108
The following is the suggested list of spare parts for a duration offive years and for up to five test sets.
The reference is made to the list of components.
1) N. 10 Fuses in the supply socket (1), rated T10A, code
XFU22101.2) N. 10 Fuses of the auxiliary DC voltage (19), rated F2A, code
XFU23109.
3) N. 1 DC to DC converter for the display (23) backlight, code
XCA10348.
4) N. 1 Encoder with switch, for MENU control knob (22), code
XCM10160.
5) N. 1 Printed circuit board INTE ON-OFF (7), code PWA11400.
6) N. 1 Auxiliary DC voltage supply module (9), code YWA11395.
7) N. 1 Auxiliary AC voltage amplifier AP-50 (10), code
PWA11396.
8/19/2019 Bo thu ro le T1000
106/108
8/19/2019 Bo thu ro le T1000
107/108
APPENDIX 2: MENU SELECTIONS FLUX DIAGRAM
8/19/2019 Bo thu ro le T1000
108/108